A data center team is deploying several NVIDIA HGX B200 8-GPU nodes into an existing colocation facility. Each rack in the facility is rated for a maximum of 30 kW, and the team wants to place as many GPU nodes per rack as thermal limits allow while keeping deployment simple. A single HGX B200 node draws roughly 14.3 kW at full load. The facility currently supplies only chilled-air cooling with no rear-door heat exchangers or direct-to-chip liquid loops available. Which action should the team take to deploy these nodes reliably?